NC-v4 EAp2:Minimum energy performance

Group Building Approch

Dear all

 

we are working with in a LEED project  with 5 building and we have used Group approach and the Exterior lighting and Domestic booster pumps are used in commonly so we have some clarification in account these commonly used facilities additionally we have prove 5% independent saving without considering renewable energy contribution for all buildings 

now the doubts are 

1.can we prove 5% independent saving for each building without considering commonly used facilities like Exterior lighting and booster pump (commonly used facilities are modelled and included in group level only )

2.Can we model this facility as prorated basis (Area based fraction) for all building

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 01/28/2019 - 14:28

I would add the common energy uses proportionally as you indicate in #2.