Hello
I'm calculating the gross floor area for my project but I'm doubtful if I should include this areas:
a) Emergency Stairs (from basements to the top level, no HVAC design for this space)
b) HVAC & MEP rooms (they have circulations for maintenance of the vertical ducts, no HVAC design for this space)
c) Storage rooms in basements (located in basements that serve as parking area, definetively not HVAC design for this space)
Thanks!
Andres Schwarz
PrincipalNRG-AR / Green Certification Consultants
13 thumbs up
January 24, 2018 - 7:47 pm
Hi, Carlos. Please be advised that PIf2 and GFA calculations differ from IEQp1 and ASHRAE 62.1 areas. Fortunately, USGBC has provideded a spreasheet with guidance on how to account for different space types. The Environmental Quality Space Type Matrix can be found at https://www.usgbc.org/resources/environmental-quality-space-type-matrix
Replying to your questions:
a) Emergency stairs: must be included in PIf2, but are excluded from IEQp1, IEQc1, IEQc3.2 (Option 2, only) and many more. Please refer to the stated document for more exclusiones.
b) HVAC / MEP rooms: same as above.
c) Storage: must be included in PIf2. Please be advised that these spaces are accounted for (or excluded from) other credits, depending on its use: food storage, inactive / unoccupied storage, OR active storage. Again, the Space Matrix provide guidance for each.
Inactive spaces are nonoccupied (defined as spaces designed for equipment and machinery or storage with no human occupancy except for maintenance, repairs, and equipment retrieval). For areas with equipment retrieval, the space is only nonoccupied if the retrieval is occasional.
You should also check on ASHRAE 90.1 gross floor area definition: "the sum of the floor areas of the spaces within the building, including basements, mezzanine and intermediate-floored tiers, and penthouses with a headroom height of 7.5 ft (2.3 m) or greater. It is measured from the exterior faces of exterior walls or from the centerline of walls separating buildings, but excluding covered walkways, open roofed-over areas, porches and similar spaces, pipe trenches, exterior terraces or steps, chimneys, roof overhangs, and similar features."
I hope this helps. Good luck!
Summer Minchew
Managing PartnerEcoimpact Consulting
LEEDuser Expert
164 thumbs up
January 25, 2018 - 8:11 am
Carlos: I concur with Andres. LEED defines Gross Floor Area as follows: "Generally, the gross floor area is the sum of the floor areas of the spaces within the building, including basements, mezzanine and intermediate-floored tiers, and penthouses with headroom height of 7.5 ft (2.2 meters) or greater. Measurements must be taken from the exterior faces of exterior walls OR from the centerline of walls separating buildings, OR (for LEED ID+C projects ) from the centerline of walls separating spaces. Excludes non-enclosed (or non-enclosable) roofed-over areas, such as exterior covered walkways, porches, terraces or steps, roof overhangs, and similar features. Excludes air shafts, pipe trenches, chimneys and floor area dedicated to the parking and circulation of motor vehicles."
Silvia Ruiz
Civil Engineer & Sustainability CoordinatorStudio Domus
8 thumbs up
January 25, 2018 - 10:24 am
Thank you very much Andres, it is totally clear to me now.
Silvia Ruiz
Civil Engineer & Sustainability CoordinatorStudio Domus
8 thumbs up
January 25, 2018 - 10:24 am
Thank you Summer!
Yanina Ibañez
ArchitectDekra
20 thumbs up
January 14, 2020 - 5:11 am
Hello! I have a question on this topic. In my project I have two basement floors, containing parking and machine rooms, changing rooms, etc. To calculate the Gross Floor Area of the project, should I discount the parking area only? Or not?
Thanks!!!
Summer Minchew
Managing PartnerEcoimpact Consulting
LEEDuser Expert
164 thumbs up
January 14, 2020 - 2:01 pm
Reference the LEED MPR Supplemental Guidance for LEED v2009 projects. Specifically the section on "How to treat parking garages" states that "Parking garages may not be included in the gross floor area of the LEED project building."
Medinah Rashid
December 7, 2022 - 12:39 pm
I have a question in relation to this. Would an unconditioned mechanical room at on the roof of the building need to be counted in the Gross Area?