FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

Green Wall

Does anyone have idea if we could model the benefit of using green wall (Vegetated)?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 03/13/2013 - 13:31

If you can model external shading with a varying degree of transparency on a schedule (assuming deciduous plants) then you can simulate that benefit. I am not aware of modeling software that could account for the cooling effect from evapotranspiration of the plants however.

Thu, 03/14/2013 - 06:29

Thanks Marcus I am an Equest-user. I know that Equest does not have such function unfortunately. Do you think we could apply a U-value to claim the benefit?

Thu, 03/14/2013 - 13:41

Perhaps I need to understand what you mean by a green wall. I am envisioning a cable system with vines growing on them. We are eQUEST users as well and have modeled that type of green wall as I described. You can account for the shading effect. The type of green wall I am thinking of or the alternative which is more densely planted really has no resistance to conductive energy loss. Same with a green roof - there is no real R-value. So there is no U-value associated with a green wall.

Fri, 03/15/2013 - 02:27

If you don't mind, is it possible to give me little hints about "varying degree of transparency"? I was doing another project that with glass fins and overhangs. But I was not able to use equest to model the effect and finally I used another program called "IES".

Fri, 03/15/2013 - 03:07

Materials in the model can be assigned a percentage of transparency. For example we attempted to simulate trees surrounding a recent project. We obtained tree heights and images of the surrounding woods. We created rectilinear boxes around the building at the proper distance. We then assigned a degree of transparency to the trees that we scheduled to change seasonally. I think we modeled something like 85% transparency in the winter and 15% in the summer. Not perfect be it should give us an idea of the effect. If you need more specifics let me know.

Fri, 03/15/2013 - 04:35

Thanks Marcus, That is really a new knowledge to me! I've spent some times on playing with equest. I am able to find out the "Blind" and the corresponding schedule. Do you refer to such? Or there is actually some hidden button for adjusting the transparency of wall? Let me try to guess your approach. The rectilinear boxes were created with all the wall set to be "window". Thus blind is assigned to reflect the transparency and schedule. Thanks again!

Mon, 03/18/2013 - 13:29

It is neither a blind or a wall or a window. Create a building shade and position it where the green wall is located. You can then adjust the transparency and change it with a schedule.

Tue, 03/19/2013 - 04:06

I got it! thanks!