Hello there,
For garage spaces that are designed for CO/NO₂ monitoring and have a neutral (Exhaust air – Supply air = 0) pressurization.
Please clarify how the average pressure differential with the surrounding spaces should be calculated.
Forum discussion
NC-2009 IEQc5: Indoor Chemical and Pollutant Source Control
Hello there,
For garage spaces that are designed for CO/NO₂ monitoring and have a neutral (Exhaust air – Supply air = 0) pressurization.
Please clarify how the average pressure differential with the surrounding spaces should be calculated.
LEEDuser is supported by our premium members, not by advertisers.
Go premium forTo post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
Jean Marais
b.i.g. Bechtold DesignBuilder Expert832 thumbs up
March 2, 2016 - 2:42 am
In this case, you don't under pressure the garage space (often it is open to outside via the ramp, so it's impossible anyway). You must overpressurise the connected spaces so that the calculation of the airflow from a connected space (which is supplied more air than extracted) to the garage across cracks, grills and door undercuts shows a pressure difference as required by LEED. In the construction phase, you could even measure it.