FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

G3.1.2.8 Design airflow rates

I have a question regarding section G3.1.2.8 of Appendix G. This section says that "design supply airflow rates for the baseline building design shall be based on a supply-air-to-room-air temperature difference of 11C". If I understand it well, for cooling mode if the room temperature is 24C then the supply air in the AHU should be 13C. The max supply air temperature, based on section G3.1.3.12 Supply Air Temperature Reset in this case should be 15.3C (13C+2.3C) - is that correct? And what about the heating mode? If the room temperature for system 5 and 7 is 21C then according to section G3.1.2.8 supply air temperature in the AHU should be 32C (21C +11C)? If this is correct then in our case the reference building will be using much more energy for heating than the design case.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 05/15/2015 - 13:26

We got a comment from GBCI that "the heating supply air delivered to each zone should be 11 degrees C higher than the setpoint" in the reference model (system 7). Could you confirm that?

Fri, 05/15/2015 - 15:37

Sounds right according to G3.1.2.8.

Mon, 05/18/2015 - 14:34

The baseline system is VAV (single duct) with reheat (system 7). The simulation program sizes the system based on cooling supply temperature - cooling mode is considered to be worse case than heating mode. That is why the temperature difference of 11C can be applied for cooling. Doesn't section G3.1.2.8 apply only to cooling mode in this case?

Mon, 06/08/2015 - 19:29

Yes. In all cases this is for cooling.

Thu, 06/11/2015 - 08:57

I'm asking about that because we received a comment from GBCI asking us to show that "the heating supply air delivered to each zone is 11 degrees C higher than the setpoint" according to G3.1.2.8 requirements. Did they make a mistake then?

Thu, 06/11/2015 - 13:37

I think so. I believe that the User's Manual has some information that clarifies this issue.