Forum discussion

CS-2009 IEQp1:Minimum indoor air quality performance

FTE vs ASHRAE 62.1 occupancy

Hi All For a C&S project there are default FTE occupancy figures that shoudl be used for water calcs, bicycle racks etc where the final occupancy is not known. These are I believe average occupancy figures that represent an average number of occupants on a typical day and are less than what we would expet to be the peak occupancy. While FTE are ok for the average usage and water/bicycle number types of calcs I don't belive they should be used for the ASHRAE 62.1 fresh air calculations. ASHRAE 62.1 has another set of default occupancy which are what I would descibe as the peak occupancy and the MEP designer will use these numbers in the MEP calcualtions NOT the FTE numbers. Has anyone encountered this issue and dealt with the fact all the online forms are trying to use the same occupancy for Fresh air calcs as the FTE? I think we should be able to use different occupancy in this case (as would the MEP designer) and that FTE should not be used fo this credit. Regards Julian

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 02/27/2012 - 22:08

The ASHRAE occupancy numbers are numbers you can use for your 62.1 calculations if you don't have exact occupancy numbers (e.g. seats on a floor plan). FTE is strictly a LEED number and doesn't have to be used for the 62.1 calculations. I've never had my occupancy numbers questioned before, but if your quantities are way off of the FTE numbers then you may be asked to explain yourself in a narrative.

Thu, 06/28/2012 - 09:49

Hi, You have a really important question to calculate required OA of VAV systems appropriatly. Refer to equation in the definitions on the page 22 of ASHRAE Standard 62.1-2007; Occupant Diversity, D = Ps/ΣPz where, Pz: Zone Population, the largest number of people expected to occupy the zone during typical usage, the ASHRAE occupancy numbers you mentioned. Ps: System Population, it should vary by less than 10% from the peak population density reported(FTE+transient) for LEED submittal. Less 'Ps', less 'Vot'. (but Ps is limited not to be over sum of Pz) Regards

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.