Hi all,I'm now working on a project under LEED certification that aims to achieve IEQc5.
Hazardous gas and chemical use areas are served by sprinkler system as a fire suppression system. If the the hard lid ceiling is drilled by the sprinkler's heads, can we assume that it is still able to demonstrate compliance with this credit?
Thanks.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Michelle Halle Stern
Senior Sustainability ConsultantGreenwood Consulting Group
120 thumbs up
February 23, 2015 - 3:10 pm
I haven't run across this issue as a problem. As long as you can demonstrate, if asked, that the gaps around the sprinklers are sealed, you should be fine.
FABIO VIERO
Head of SustainabilityManens S.p.A.
18 thumbs up
March 19, 2015 - 10:06 am
Thank you so much!