FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

Fenestration SHGC for proposed model

Dear community, According to tables 5.5-1 (climate 1a), the Solar Hear Gain Coefficient for the proposed building should be no more than 0.25. Is this a requirement for the proposed building? I was wondering if there's a possibility to trade off some SHGC (i.e. allow a bigger SHGC) with other design options - such as reduced glazing areas for example? Your help will be greatly appreciated. many thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 06/07/2013 - 16:26

The SHGC is not a mandatory provision and is therefore not required for the proposed. SHGC can be traded (you can exceed the prescriptive value as long as you achieve enough savings in other areas). It cannot be traded for window area as this must be identical in both models (unless the proposed exceeds 40% window to wall then the baseline is 40% and the proposed is as designed).

Mon, 06/10/2013 - 08:33

Marcus, many thanks for your input. I was also wondering if there's flexibility in the R values for the roof assembly/insulation level? Table 5.5.1 appears to limit the resistance of the roof assembly to a Uvalue of 0.19 W/m2K (SI system) - and a Rvalue of 5.3 m2K/W (SI) for insulation alone. Can the proposed building have less insulation than what table 5.5.1 suggests? Many thanks in advance. Ioannis

Mon, 06/10/2013 - 12:39

Yes. All of the prescriptive values in the 5.5-X tables are available for tradeoff.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.