I’m modeling the proposed design model and in order to compare it with the baseline model I want to calculate the F-factor of the slab-on-grade floor according to table A6.3 of ASHRAE 90.1-2007. I’m using the SI edition. It is a heated/cooled slab, the entire floor surface is insulated horizontally, and the thermal resistance R-valued of insulation is equal to 4.1. Therefore I would consider “heated slab” -> “1200 mm horizontal” and since there is no F-factor for R-value equal to 4.1 as F-value I would consider the minimum value of that line, i.e. 1.92. Am I right? Regards
If you have a heated slab (contains piping or other heating/cooling elements) and it is entirely insulated you would use the row labeled "Fully insulated slab" at the bottom (at least that is what is in the IP edition). If you R-value is under R-5 I would interpolate based on the increments surrounding R-5.