EBOM-2009 IEQp1:Minimum IAQ Performance

Ez for projects unable to meet ASHARE 62.1-2007?

Hello. Is it necessary to consider the zone air distribution effectiveness (Ez) for projects unable to meet ASHARE 62.1-2007 when calculating 10cfm/person minimum ventilation? Thanks in advance,

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 03/21/2014 - 16:16

No, you do not need to consider Ez for air handling units unable to meet ASHRAE 62.1-2007. The 10 cfm/person is as measured at the AHU outdoor intake. However, you do need to evaluate each AHU separately to determine whether it can meet ASHRAE 62.1-2007, prior to using the 10 cfm/person alternative. You may need to submit some AHU's through the ASHRAE 62.1-2007 path while others in the same building use the 10 cfm/person route.

Mon, 03/24/2014 - 01:21

Thank you very much, Julia!