NC-2009 SSc6.1:Stormwater design - quantity control

Example 2 in ref guide

Hi, there has been some previous discussion in this topic, but no definite answer has been given. Example 2 in the ref. guide uses 1" storm, referring to it as 90% of the average rainfall event. However, the credit requirement for SSc 6.1 requires the usage of the 24hr storms. It is quite confusing whether this calculation would meet the requirement, which they give as an example. Can we use the 90% of the annual rainfall events??

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 06/04/2014 - 17:03

This credit uses the 1 and 2-year 24-hour design storm for your project area. That example simply shows that the raingarden being designed, holds the volume of 1" runoff, which coincidentally is the 90th percentile storm. The examples do not set the credit requirements, the requirements page does that.