We have a project in Dubai targeting LEED Gold certification under LEED V4.1 BD+C New construction. As a green building consultant, we have planned to consider ASHRAE 90.1.2013 to create the baseline energy model as mentioned in the LEED Interpretation 10488: ASHRAE 90.1-2013 in LEED v4.1 BD+C, (https://www.usgbc.org/leedaddenda/10488)
Kindly request your feedback on the following queries:
- Is it acceptable to consider ASHRAE 90.1.2013 to determine the energy cost and greenhouse gas emission savings for LEED v4.1 project as mentioned in LEED Interpretation 10488?
- If acceptable, can we calculate the cost savings directly like: % of improvement = (Baseline building performance – proposed building performance) / Baseline building performance) as followed in LEED v4?
- If on site renewable energy produced, then we can subtract in both cost and green house gas emission, to achieve points in both cost and green house gas emission table. Please confirm.
- Can we consider, Renewable Energy Certificate (REC) purchased for the project to get points from Greenhouse Gas Emissions (Table 2)
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5934 thumbs up
August 7, 2020 - 10:52 am
1. yes
2. yes
3. yes
4. no, it appears that Tiers 1, 2, and 3 count but not 4 or 5.
Amal Venugopal
Project Manager8 thumbs up
October 19, 2020 - 5:11 am
As per LEED Addenda 10488,
can we consider renewable energy to meet Prerequisite? [7% for New Construction (except Healthcare, Schools, Multifamily Residential)]..
Thanks...
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5934 thumbs up
October 19, 2020 - 10:04 am
It is my understanding that the project must demonstrate compliance with the prerequisite without renewables. Renewables then count toward the percent improvement beyond the minimum requirement.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5934 thumbs up
October 19, 2020 - 10:15 am
Upon further reflection it does appear that some renewables can count toward the prerequisite compliance, those that meet the criteria in G2.4.1.
S S
June 7, 2021 - 5:53 am
Is this LEED Interpretation 10488 applicable internationally? Please refer the contents copied from https://www.usgbc.org/leedaddenda/10488
Credit NameEA103 - Minimum Energy Performance
Credit CategoryEnergy & atmosphere
International Applicable: No
Campus Applicable: No
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5934 thumbs up
June 7, 2021 - 11:00 am
I don't see why not if you are using 90.1 to demonstrate compliance.