Forum discussion

EBOM-2009 IEQp1:Minimum IAQ Performance

EBOM IEQp1-A1 Statement "Would need over 100% OA Intake"

Our EBOM 2009 project credit data has to be completed by 8-5 and I am getting a message "Would need over 100% OA Intake" at the end of the IEQp1-A1 VAV data input form. All values look good with the measured OA intake to the AHU exceeding the required minimum amount. What does the over 100% OA statement mean? We are using the V4 form.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 07/30/2014 - 21:31

Look for the zone in purple italics in the calculator. Is it getting enough ventilation? Your "critical zone" may be under ventilated. Also, which cell is this message showing up in? If it's showing up in row 43 of the USGBC version of the ASHRAE calculator, it may mean that you meet the prerequisite minimum OA, but not the 30% increased OA for IEQc2.

Wed, 07/30/2014 - 22:25

Ilona, I am referring to the LEEDonline "VRP Compliance Calculator" found in Appendix 1 of the V4 data entry form. We are not using the ASHRAE calculator "62MZCalc". The critical zone had a Zp of 0.99 so I changed some values an now the highest Zp is 0.93. The note is removed when I hit recalculate but comes back when I reload the saved form!! :-(

Mon, 06/13/2016 - 23:16

Hi James! I have the same issue filling out the IEQp1 form. How did you solve it?

Thu, 12/15/2016 - 22:53

I contacted the GBCI and they replied that I should use the "special circumstances" section to notify the reviewers about this glitch in the form. I hope this will help other project teams!