Does anyone out there know what the following comment pertains to:
Provide additional information (Mech-5C report) to verify that the Proposed Case Carrier units have been modeled at a 50% minimum CFM ratio, consistent with equipment specifications.
Our mechanical engineer has modeled this equipment at 30% and I cannot find anyhting in the reference model that provides me with more information.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
August 28, 2013 - 12:45 pm
I assume this is a LEED review comment.
Sounds like the reviewer saw the 50% value somewhere in the documentation provided for the project (maybe in the information uploaded in PIf4). They then compared it to what was modeled and noted a discrepancy. So you either fix it in the model to be consistent with the documentation or explain why the two values do not match.