Forum discussion

NC-2009 EAc1:Optimize Energy Performance

EAc1 Space Cooling and Heating

Hello, When I generate the EAc1 Summary Report in HAP I have a negative percent savings in space cooling and heating in the performance rating table. Is the space cooling and heating energy and demand based on the space inputs and system inputs? If so, shouldn't I be seeing a positive percentage since the inputs for proposed are more insulated? Thanks!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 07/07/2017 - 14:12

Hi Mark, There might be other factors other than the insulated envelope that has an impact on the negative saving percentage. Look through the HVAC systems which might be consuming more kWh or Therms, also double check the T-stat schedules which should be identical between the two models (Baseline & Proposed). You can ONLY relate the savings to the envelope material if this is the ONLY difference between the two designs. Also, I would recommend you sharing your questions regarding to HAP on their forum by email (hap-users@lists.onebuilding.org). Good luck

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.