We have a hotel where the showers have two showerheads. One showerhead placed overhead and one han-held showerhead. They have different flow-data.
Both showerheads will be used, but we do not know how much each of the showerheads will be used.
Which flow data shall we use? The highest flow or the average flow, or?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Michelle Robinson Schwarting
Re:Vision Architecture138 thumbs up
June 15, 2015 - 7:46 am
I believe you need to use the worst-case scenario (the highest flow rate). Along those lines, if they can be used simultaneously, I believe you'll need to add the two rates together...