NC-2009 EAc4:Enhanced refrigerant management

documentation toolkit

i was looking at the uploaded cutsheet under the documentation toolkit, and it doesn't look that piece of equipment is meeting the credit requirements. For instance, it is a 1.5 ton unit with R-410A refrigerant, and a Rc of 2.5. When you enter that into the calculator, it is not under 100 for the average refrigerant impact per ton. Am I missing something?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 05/17/2018 - 00:50

Hi Courtney, the credit looks at the average across all refrigerant-containing equipment in the project. A given piece of equipment may exceed 100, but if enough units are under 100, the project can still achieve the credit threshold.