I am modeling a new building on a university campus following LEEDv4 Option 1, Whole Building Energy Simulation. Heat Recovery Chillers are providing 44% of the cooling load of the building and the rest of the load is provided by campus chilled water. Heat recovery from the chillers is the primary heating source for the building with campus steam providing what cannot be met by heat recovery. Which path from the LEEDv4 Reference Guide for District Energy Systems should be followed for HVAC systems that use campus systems for partial loads? How is the ASHRAE 2010 Appendix G baseline modeled when the proposed model uses partial energy from a district energy system? Does the baseline model need to be modeled with 44% on-site equipment with DES back up energy as well same as the proposed model? Thanks!
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
- Based on the building type, ASHRAE 90.1 2010 and all electric HRC system, the baseline system would be system 6. Could you please confirm. I see that in 2013 ASHRAE, the baseline system type selection is based on climate & not the heating/cooling source. Is there an addendum to meet the newer code?
- Since, the CHW is supplemented for peak load, are we supposed to use DES guidelines assuming CHW & HW coils instead of DX coil. In that case, the baseline system would become VAV reheat (system 8). Since the proposed HRC is feeding back into the campus, we would be penalized for using an efficient system and adding back to the campus if we were to use System 8
- If I had to use DES system path 2, how should I model the baseline & proposed case? Proposed model =Cooling, Campus Chilled water system and HRC; Heating, Natural gas boilers at campus & HRC at building level and baseline would be as per Appendix G?
Add new comment
To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.