I am working on an underground building project aiming for LEED NC gold/platinum. Project design feasibility showed that 25% energy saving can be achieved with little effort as the HVAC design parameters were selected taking into account of sustainability and energy saving targets. Project considers district cooling plant chilled water as cooling source with no heating source in the design. District cooling is considered in the design to achieve the energy saving target as the project location pushed the client to not to go with water - cooled chillers due to limited water availability.
We opted for option 2; reasoning being the point cap when considering option 1 and our targeted point for EAC1.
Our project’s design parameters are quiet efficient in terms of envelope (don’t think it will affect the saving as the project building is almost 80% underground), efficient HVAC systems (ERU units with FCUs and with district chilled water system). Due to un-availability of DES details, we considered 4.4 as plant COP for proposed case as per the assumptions referenced in ‘Treatment of District or Campus Thermal Energy in LEED V2 and LEED 2009 – Design & Construction’. Baseline is done based on ASHRAE 90.1-2007 with System 8 and chiller of 6.1 COP. The results are not as expected showing a different pattern. I have some questions which are listed below.
1. Is there any way to model the proposed system to account for cost of the energy source i.e. to account for the impact of chilled water/energy cost alone?
2. Comparing a water cooled chiller with 6.1(COP) in Base with 4.4 plant COP for proposed doesn’t look fair. When we calculated the overall plant COP for Base case it comes around 5.5 a much higher COP than 4.4(proposed plant COP). But in actual cases, district chilled water plant is much more efficient than a standalone chiller. This questions the performance of the district chilled water systems and opting out from such options. Correct me if I am wrong.
3. In general, water cooled chillers are not a feasible option in very hot and humid condition. Projects will opt for air cooled chillers or district energy systems in these areas. A COP of 6.1 with water cooled centrifugal will prove both the options less efficient in terms of energy savings. Correct me if I am wrong.
4. I am modelling my project based on the document referenced above. Is there any other option or method which is accepted by USGBC to do simulation with district chilled water systems.
5. What are all the areas, I need to check in my energy model to make sure of the system and plant side parameters for this scenario?
I can understand my questions might take lot of your time. But you suggestions and comments will help me a lot.
Thanks a lot for your time.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5915 thumbs up
April 20, 2015 - 11:13 am
1. Not sure I understand the question
2. The default efficiency is low on purpose because some DES plants are inefficient so using the low value is conservative and encourages project to determine the actual plant efficiency.
3. That sounds right but there is no exception for hot/humid climates.
4. You can use ASHRAE 90.1-2007 addendum ai which treats the chilled water as purchased energy and eliminates the point floor and cap.
5. This would vary depending on the software.
rodd borgogno
mechanical engineerstate of californiat
April 20, 2015 - 1:07 pm
I am actually trying to determine the COP of our cooling only DES plant.
We are measuring the Energy used by the plant (KWh) , and the energy produced by the plant (BTUh).
Question: If I have a years worth of data, can I just use the annual BTUh divided by the annual KWh to determine the average annual COP of the plant, and then use this COP in my energy model?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5915 thumbs up
April 20, 2015 - 2:35 pm
See Appendix C in the DESv2. Your method seems to be in alignment with one of the allowable methods.