FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

DCV requirement for high-occupancy areas

Hello! We have a canteen project in Shanghai. The building has three floors, total GFA is 64,067 square feet. The baseline HVAC system type is system 6. In the second floor, there are only two air conditoned zones, dining area (12,588 sf2) and restroom (415 sf2). The dining area need to use DCV in baseline system. We have two questions about the model of eQUEST: 1. Do we need to use system 4 for the dining area and system 6 for the restroom? or both use system 6? or system 6 for the dining area and system 4 for the restroom? 2. Shall we use the minimum ventilation rates for the baseline system?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 04/05/2016 - 14:48

1. See Section G3.1.1. For a system 6 you need to model it in the baseline as a system per floor. You also must apply any of the applicable exceptions to G3.1.1. 2. The ventilation rates must be identical to the Proposed unless the Proposed has DCV.