Dear forum,
I hope the following help request is falling under the right LEED version, since the calculations I am running are following the guidelines of CS2.0 as the design studies of the building were started in 2008. I am using the OPTION 2 - Daylig simulation Model.
The 30 floor office building is located in a dense urban area with immediate adjacent buildings in the context.
The guidelines say : "calculate the daylight illunitation for each applicable space using the following criteria: clear sky conditions at 12:00 noon on the equinox(s) for the project specific location".
Each floor are the same design except the first 5 floors.
Since the design has to achieve more than 75% of the total regularly occupied spaces with a minimum of 25 fc, and since this is a weighted average area calculation of the different daylit zones, it sounds crazy to run each separate floors being really time consuming. Is there an alternative way to take some low-mid-high level typical floor to run the calculations and assumed this is a fair representation of the overall building simulation ? (similar to the floor multiplier when running and energy model).
The concern is that every floor has a different DF then since the adjacent building are smaller than the as designed office.
Also I assume the context needs to be modeled as it plays an important shading mask role impacting the illuminance map of the floor.
Thank you for your valuable feedback.
Olivier.
Eddy Santosa
Director of SustainabilityDBR Engineering Consultants
376 thumbs up
October 18, 2013 - 7:31 pm
Olivier,
Yes, you can use the typical floor approach based on ID#10253. I will recommend to choose the worst case scenario to avoid any question.
Olivier Brouard
Sustainable Energy EngineerOctober 29, 2013 - 8:41 pm
Thank you Eddy.