I am trying to find out if there is a situation where the CxA on a project can be a part of the same company as the deign team but has not been a part of the design effort? The CxA is strictly chosen for the commisioning effort. Is this allowed in any case. I am aware of a potential conlict of interest here but just want to know if the agent is not a part of the Design team is there a case where this is acceptable. Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 10/05/2021 - 14:00

Hi Decorda, there was a recent LEED addenda on this subject: https://www.usgbc.org/leedaddenda/5000127    "If the CxA is an employee of the design or construction firm, upload documentation confirming: that the CxA has no responsibilities related to project design or construction; the CxA is reporting all findings to and communicating directly with the building owner; and the owner has signed off on this arrangement."   I don't know exactly what "documentation" the reviewer would be looking for, whether that means just a narrative or something more formal, but that's the latest. 

Tue, 10/05/2021 - 18:31

Thanks Emily. This helps a lot in just knowing that this could be a potential path forward.  

Wed, 10/06/2021 - 05:19

Hi Emily and Decorda, I would demonstrate compliance with a Declaration Letter signed by the CxA.