Hello to all LEED Users,
My proposed building has following percentage of glass at each orientation:
NE: 90% percentage of glass
SE: 90% percentage of glass
NW: 90% percentage of glass
SW: 0% percentage of glass
What will the percentage of Glass be at the baseline building:
Thought 1:
NE: 40% percentage of glass
SE: 40% percentage of glass
NW: 40% percentage of glass
SW: 0% percentage of glass
OR
Thought 2:
NE: 40% percentage of glass
SE: 40% percentage of glass
NW: 40% percentage of glass
SW: 40% percentage of glass
Or
Something else?
Thank you very much
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5925 thumbs up
June 16, 2023 - 9:56 am
Why does the SW have 0 glass in the proposed?
Konstantina Kalliakoudi
Mechanical Engineer13 thumbs up
June 16, 2023 - 12:30 pm
Hello Marcus,
The proposed is the way the real building is designed, isn't it?
At the SW the Architects of the project have no Glass....only wall
Is there a restriction on that?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5925 thumbs up
June 16, 2023 - 12:49 pm
Sorry I wasn't clear about why I was asking. Yes the proposed needs to reflect the design. What I was really wondering is whether there was another building up against the SW side as that would make a difference in how you should approach it. If there is not a building or something else against that facade and this was just an architectural design choice then thought 2 is the correct approach. If there is a building against the SW then thought 1 is correct.
Konstantina Kalliakoudi
Mechanical Engineer13 thumbs up
June 23, 2023 - 4:20 am
Thank you Marcus,
You helped me a lot!!!!