FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

control of PIU fans for System 8

Shall the PIU fans of System 8 cycle according to paragraph G3.1.2.4? In EneryPlus you can impose the "Fan On Flow Fraction", which is defined as: The fraction of the primary air flow at which fan turns on. In the parallel PIU the fan operation is intermittent. If the primary air flow is above this fraction of the maximum, the fan is off. Otherwise the secondary fan will run according to the Availability Schedule specified in the Fan:ConstantVolume object (see Fan Name below), unless it is overridden by an availability manager (ref. AvailabilityManager:NightCycle and others). Could the "Fan On Flow Fraction" be equal to 0.5 and the fans be always available? In this way they are continuously on during the winter season and they turn off sometimes during the summer season (when more primary air is required).

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 08/16/2016 - 17:50

The PIU fans should not cycle according to G3.1.2.4. This applies to the main fans in the air handling units. The PIU fans should operate when the primary air flow has reached the minimum setting. The minimum flow is 30% as indicated in G3.1.3.14. So the fraction should be 0.3.

Wed, 08/17/2016 - 18:29

It means that during the winter season (when no cooling is requested) the PIU fan shall operate 24 hours/day, doesn't it?

Mon, 08/22/2016 - 20:48

It shouldn't. The PIU fan should cycle based on the temperature in the space. It should also be off when the space is unoccupied unless there is a call for heat. The main air handler fans should operate during occupied to meet the minimum outside air requirements. This document on pages 3.97 to 3.98 explains how the system fan control should operate. http://www.pnnl.gov/main/publications/external/technical_reports/PNNL-25130.pdf

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.