Forum discussion

CS-2009 IEQc7:Thermal comfort - design

Control devices required for meeting ASHRAE 55

Dear Leeduser.com members. We have a question regarding whether we need these controls for meeting LEED credits under v2009 CS version. - Radiator heating system. Valves are automatically controlled to room temperature. Questions: Do we need any heating control? Is it enough to have local valve control devices? Thank you for your reply. BR, Mindaugas

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 01/12/2017 - 23:19

Local controls like hand valves typically would not comply with meeting ASHRAE 55, but it has been a while since I had dived deep into the standard. In general, the goal of this credit is to show that the systems were designed to meet and control to provide comfort to the occupants in all design conditions. If heating is required to meet those conditions, then some sort of automatic control would be required.