Working on a warehouse project and we had two products that we were unsure about. There is a Bond Breaker and a concrete curing compound. Both products get applied to the concrete but manufacturer says reacts within the concrete to create a new pdocut that does not off gas. There is no membrane or residual that is formed on the concrete itself. Would these two prodcust need to categorized with the coatings category along with the Densifier??
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Dave Hubka
Practice Leader - SustainabilityEUA
LEEDuser Expert
532 thumbs up
September 21, 2023 - 12:53 pm
Rating System Correction #100002609 dated April 21, 2023 allows/requires poured concrete to be excluded from the flooring category:
https://www.usgbc.org/leedaddenda/100002609
wet-applied products on the concrete are to be included within the paints and coatings category. Aerosol applied products are not addressed by the referenced standards or the credit language, but i have heard from other folks that gbci is requiring aerosol applied products to also be included in the credit compliance.