NC-2009 IEQc4.1:Low-Emitting Materials—Adhesives and Sealants

Concrete Adhesives - which limit to spec?

We have the following materials called out in the 03 30 00 Cast-in place concrete spec: 1. Semi-rigid joint filler 2. Bonding Agent 3. Epoxy bonding adhesive When/where these are applied inside the weatherproofing membrane of the structure - which category do they fall under for specing the VOC limit? We are struggling with adhesive/sealant products specific to Concrete use.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 03/08/2013 - 19:34

Hello I don't know if this is directly helpful, but within my guide spec for concrete, it says: Liquid floor treatments shall have a VOC content of 200 g/L or less Curing and sealing compounds shall have a VOC content of 200 g/L or less For joint filler, you might consider using the following: Sealant Primers for Porous Substrates: 775 g/L Other Sealants: 420 g/L Epoxy is much trickier, as it exceed allowable VOC content for LEED projects. I believe you can still use an 'epoxy allowance' if there is no other product option for the application.