I’m helping out a project team in Italy with their LEED project. This is a mid-rise residential building that has a 2-story underground parking garage. It has, besides the main entrances (directly open to the outside) an open ventilation shaft on each parking floor that is connected to daylight (open terrace on ground floor). First of all, does the parking area need to meet the requirements of the IEQ prerequisite 1, since it is not "regularly occupied"?
Secondly, the garage is designed to have an exhaust system in each garage floor with CO and CO2 sensors that is set to go off only when the CO and/or CO2 levels are above a certain set pint. In other words, it will exhaust only "when needed". Would this be enough to satisfy the credit?
I would appreciate any guidance on this! thank you
Roger Chang
Principal, Energy and Engineering LeaderDLR Group | Westlake Reed Leskosky
LEEDuser Expert
398 thumbs up
October 27, 2010 - 9:14 am
Patrik, your main focus will be on the exhaust system to maintain acceptable CO levels. Please reference Table 6-4, which requires an exhaust rate of 0.75 cfm/sf, unless there is a certain openness factor to the outdoors. Local codes may require different rates.
Patrik Lazzari
10 thumbs up
October 29, 2010 - 7:28 pm
Thank you Roger. Could I operate the fan system intermittently with the CO sensor OR an occupancy sensor; or do i have to run the fans continuously?
If using the CO sensor, what would be the right threshold (ppm)?
thank you!
Roger Chang
Principal, Energy and Engineering LeaderDLR Group | Westlake Reed Leskosky
LEEDuser Expert
398 thumbs up
December 2, 2010 - 8:49 pm
Patrik, operation really depends on the applicable code. 15 ppm is the recommended maximum limit for CO.