Complying with 62.1 in an Undergroung Garage

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 10/27/2010 - 13:14

Patrik, your main focus will be on the exhaust system to maintain acceptable CO levels. Please reference Table 6-4, which requires an exhaust rate of 0.75 cfm/sf, unless there is a certain openness factor to the outdoors. Local codes may require different rates.

Fri, 10/29/2010 - 23:28

Thank you Roger. Could I operate the fan system intermittently with the CO sensor OR an occupancy sensor; or do i have to run the fans continuously? If using the CO sensor, what would be the right threshold (ppm)? thank you!

Fri, 12/03/2010 - 01:49

Patrik, operation really depends on the applicable code. 15 ppm is the recommended maximum limit for CO.