We have a Market space fit-out that has multiple tenants within the this market space (multiple food vendors and restaurants). Some of the tenants will have space fit-out in the overall market scope of work, however some of the tenants will be providing their own fit-out and equipment at a later date. If the project is pursuing the prescriptive path to meet the prerequisite, does the commercial kitchen equipment have demonstrate compliance with Appendix 3?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $15.95 »
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5925 thumbs up
September 28, 2018 - 10:03 am
Is the project a tenant space with subtenants? Sounds like some sort of hybrid CS-CI project.
Under the prerequisite the applicable equipment must be Energy Star compliant. It appears that Appendix 3 include the Energy Star minimums for the prescriptive path.