Dear all,
Once I saw a LEED Interpretation stating that small spaces, or private offices, could be exempt of installing CO2 sensors to comply with this credit, for CI only, not to NC.
I can't find the LI now. Can someone help me with the number of the LI? And is there a similar interpretation exempting us to install CO2 sensor in private offices for NC?
Regards,
Anderson
Michelle Halle Stern
Senior Sustainability ConsultantGreenwood Consulting Group
121 thumbs up
February 19, 2016 - 8:54 am
I'm not aware of an LI, but you only need sensors in densely occupied spaces of 25 people within 1000 s.f. For a 100 s.f. office to need a sensor it would have to accommodate 3 people. Is that your situation?
CT G
23 thumbs up
February 19, 2016 - 12:08 pm
Thank you for your reply Michelle.
Yes, our situation is similar to what you described. We have a 25 s.f. space with one person.
Michelle Halle Stern
Senior Sustainability ConsultantGreenwood Consulting Group
121 thumbs up
February 19, 2016 - 4:35 pm
I did a little digging and the only thing I found was a post in LEEDUser saying that there is not exception for CO2 monitors is rooms with fewer than 10 people. (Vamshi Gooje Nov 21 2011 in response to a question from Dylan)
Though I'm not sure what the source of this information is.
I think your situation is worth submitting a CIR. It seems a little overkill to provide a CO2 sensor for such a small space serving one person. However also consider how long this person is in this 5'x5' space. Is it really regularly occupied or just used intermittently? If I was stuck in a 25 sf space all day I'd feel better knowing that fresh air was being brought in if the CO2 levels were elevated.