CI-2009 IEQp1:Minimum indoor air quality performance

CI IEQ p1 - Template Table

Do we have to use the template table or can we upload our own spreadsheet using the same calcs? The template spreadsheet takes much more time than our spreadsheet that is used during the design phase.

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 02/21/2011 - 16:43

If you are uploading your own spreadsheet, make sure you still include the information required in the template (i.e. for each ventilation zone, the amount of outside air required by ASHRAE 62.1-2007 and the actual amount of outside air provided to that zone). Just showing the outside air volume required and provided on a system level (per air handling unit) for multi-zone systems is not sufficient.