At issue, our proposed system (chilled water) is paired against a System 5 (non-residental < 5 floors & 25,000 < SQFT < 150,000) but we are having a problem with the energy modeling which was confirmed by the Carrier HAP customer support personnel. The way ASHRAE 90.1-2007 derives the compressor + cond fan kW from the full load EER is a bit flawed and ASHRAE has recognized this. This results in the Packaged DX RTU being a far more efficient system compared to a chiller operating at the same EER. This is because the RTU total energy includes the indoor fan energy and the chiller energy does not. When you subtract out the indoor fan kW allowance from the RTU the resulting compressor + condenser fan kW of the RTU is much less than the chiller.
Summary: Because of the nature of the code and how software interprets it, it seems untenable to pit a chilled water system that does not include fan energy in its EER calculation against a DX packaged system that does include fan energy.
Request: We would like to pair up our proposed chilled water system again System 7 for a more logical comparison. This is my first foray into the LEED online portion, does anyone know how I go about getting a formal answer?