Forum discussion

CS-v4 EAp2:Minimum energy performance

Chilled beams with default occupancy

Hello,

We have an office building designed with DOAS CAV (20degC ) and active chilled beams with induction factor of 4 (at 18.5degC). The fresh air for higenic reasons is 40m3/h*person, however it has been increased to 50m3/h*person in order to make the active chilled beams work to cover peak space cooling load.

The design occupancy is 6m2/person. The designed system with design occupancy provides low summer unmet hours due to high supplied air volume working together with the active chilled beams. 

However, for CS LEED compliance, we have been asked to change the occupancy to default values (23m2/person). if we use 50m3/h*person with lower occupancy, the active chilled beams are not able to cover the peak summer gains. Therefore we will need to supply around 150m3/h*person to keep the active chilled beams working in order to cover the cooling loads with high solar gains. This means that even with lower occupancy (23m2/p), the total supplied fresh air is quite similar to the case with 6m2/p. 

At the same time, the baseline case is modelled with a VAV system 7. I understand that the baseline case should be modelled with the outdoor fresh air per person as per local regulation and does not have to the same as the proposed case (in our case 40m3/h*person).

In this case, the building performs much worse when using 23m2/person than when using 6m2/person because of the required air with lower to make chilled beams work.

I would like to ask what is the best approach in this case. 

- Should we model with 6m2/p as per desing specifications, or with 23m2/p as per CS default occupancy to match other LEED credits?

- if we use 23m2/p, how can we overcome the issue with active chilled beams and worse performance compared to the baseline case than when using 6m2/p?

Thank you in advance.

Regards,

Manuel

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 08/21/2020 - 15:34

Are you specifically being asked to apply the default occupancy within the energy model? If you can provide supporting justification for the design occupancy as a realistic value for the anticipated operation of the building, and this value was used to design the DOAS, then it should be used in the model. The Baseline outdoor airflow should be modeled as the local requirement, calculated using th same occupancy as the Proposed case.

Thu, 04/15/2021 - 08:36

Hi Tyler, Yes, we have been asked to use default occupancy for our energy model since it is the approach our client follows in all their projects. Previously, for other projects, I have always set the models with the design occupancy. Therefore I would like to understand how this approach with default occupancy would work: a) is it the right approach to use default occupancy if our systems (heat/cooling source, AHUs, etc) have been designed for 6m2/person? b) in our design we have a flow rate of 43m3/h*person (reduced finally from 50). This design rate was used for sizing the AHUs. If we change occupancy in the energy model to default, should we still apply this air rate per person in the proposed case even though it will give a much lower total outdoor air volume in the model compared to the one in the AHUs design? could this be a potential discrepancy that the LEED reviwer will comment on?. c) what about heating and cooling sources? with less occupancy the peak demands will be much lower than the equipment designed. d) how this should be aligned with the IEQp1 credit? I believe we should have the same occupancy and air volumes for indoor quality credits and energy model (and also WE credits). thank you.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.