Forum discussion

CI-2009 IEQc4.5:Low-Emitting Materials—Systems Furniture and Seating

Chamber Concentration or indoor air concentration?

I have a SGS test report of several furniture using ANSI/BIFMA M7.1-2007 method. The test results have two different table. First one is VOCs concentrations in 1 Cubic Meter from system furniture, which is called Chamber concentration. In this table, Formaldehyde is 67.4 ppb which is higher than limit. But the second table says: "According to concentration in 1 cubic meter chamber to calculate indoor air concentration", and the result is 4.5 ppb for Formaldehyde, which is under limit. For my understanding, the second table is the result we should use to do the comparison with Limit. But I have a concern here if the table one will impact the review process. Did anyone meet this situation before? Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 12/20/2013 - 16:36

Hello Qiang, It's difficult to say without reviewing the actual report, but I would assume the concentrations found in "Table 2" would reflect direct-scaling or extrapolations to Open/Private Office Settings, or LEED for Schools modeling. Your report should indicate if these test criteria are applicable, depending on your project requirements.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.