FAQs about EAp2 :

Our building includes a large laboratory space. Can our project benchmark under the Labs21 program?

We have an international project and the space type is eligible for an Energy Star rating. Can we pursue Case 1 to demonstrate compliance given the recently released alternative compliance paths for international projects?

We have a number of buildings on a single campus that we would like to certify at the same time. Is it possible to benchmark the buildings at the campus level?

I have a mixed-use building and am wondering if it is possible to pursue the prerequisite through Case 1. How do we proceed?

We have a building that consists of two attached structures and it’s unclear if we have to consider it a single building or if it should be certified as two separate buildings and benchmarked accordingly. How should we proceed?

How long is an Energy Star label valid to use with a streamlined approach for Case 1?

Our building includes heavy process loads that significantly increase the overall energy use in the building. If we submeter these loads, can we exclude this energy use for benchmarking purposes?

We have installed submeters on our building but the utility bill includes energy use from several other buildings located on the same campus. How do we reconcile this during the LEED review process?

When is it possible to exclude up to 10% of the building from EAp2?

What do I do if the number of building occupants, operating hours, or vacant space changes during the performance period?

If you pursue the streamlined path for an Energy Star label, should the performance period for EAc6 match the 12-month time frame of the label?

How do I account for computers with multiple monitors on Portfolio Manager?

How should I treat vacant space on Portfolio Manager?

View answers »

Forum discussion

EBOM-2009 EAp2:Minimum energy efficiency performance

Central Chiller Plant - Chilled Water Btu Metering

A central chiller plant supplies chilled water to our project building and several other buildings. In order to generate the Energy Star report, we are required to input the chilled water energy consumption in Btu. With reference to the following equation, instead of having the Btu meter directly, would having both a temperature sensor and a flow meter installed on the chilled water suffice? 500 x Flow Rate [gal/min] x Delta T [F] = [Btu/h]

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 06/23/2011 - 23:29

Jason: In principle that would be fine - LEED does not care how your metering is set up, just that you're measuring (and recording) the energy flowing into your building. My one suggestion is to ensure that the quality of the metering and data logging is good enough. If you're measuring supply & return temperatures and water flows separately, just make sure you're doing it properly and robustly so you'll get accuracy and precision similar to what a dedicated, unified BTU meter would provide. Mike