FAQs about EQp1 :

We have a VAV system where single AHUs serve multiple zones. Do we need to take outside air measurements at each VAV box?

Our building has a single fan that supplies outside air to multiple AHUs. Do we need to perform outside air testing at the supply fan or at all AHUs?

What if our systems do not meet the required outside air when systems are tested at worst-case conditions?

What if after our Preliminary Review we have to revise the ventilation rate procedure calculations and find that we need to make corrections to the system in order to meet the prerequisite? Can we redo the outside air testing after making corrections? Wou

My building has 80 AHUs providing ventilation to building spaces. Do I have to do the ventilation calculations and conduct outdoor air measurements for each one?

Our system cannot provide enough outdoor air to meet ASHRAE 62.1-2010 due to design limitations. How much outdoor air must we provide to meet Case 2 instead?

The outdoor air intake for our ventilation system is not accessible, and it’s not possible to measure the outdoor airflow directly. How can we determine the outdoor airflow for this system?

How do I find whether my project is located in a non-attainment area for particulate matter or exceeds the prerequisite ozone requirements?

What happened to the IEQ Space Matrix that was available to version 2009 projects? What should I reference to determine how spaces in my building should be categorized for this prerequisite?

View answers »

Forum discussion

EBOM-v4 EQp1:Minimum indoor air quality performance

Case 2. Systems unable to meet required outdoor airflow rates

I don't understand Case 2.

If meeting the outdoor airflow rates in Case 1 is not feasible because of the physical constraints of the existing ventilation system (...). Supply the maximum possible to reach the minimum setpoint in Case 1 

How can the minimum setpoint in Case 1 be reached if "meeting the outdoor airflow rates in Case 1 is not feasible"? Probably I'm misunderstanding the meaning of "minimum setpoint".

Best Regards

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 03/30/2018 - 20:09

Hi Francesco, for Case 2 you need to supply at least 10 CFM per person, and then beyond that you're asked to "supply the maximum possible to reach the minimum setpoint in Case 1". So they're basically saying, if you can supply something in between the 10 CFM minimum, and the minimum requirement for Case 1, then you need to do that. You don't have to reach Case 1 but you have to get as close as you can, after hitting the 10 CFM requirement. Does that help or confuse things more?

Wed, 08/23/2023 - 09:41

Hello, would this also apply to extraction requirements when systems are unable to meet the required exhaust rates?