December 16, 2015 - 11:08 am
Entering only "office" into the calculator most likely won't be accepted by the LEED reviewer.
When we do not have tenant build out plans we physically walk the space and measure potentially critical zones to enter into the 62MZ.
Hugo Teixeira
Grupo OrionFebruary 15, 2016 - 1:43 pm
Hi David ,
I Understood your answer , but I would like to know if I must carry out the mesuruments for each zone in order to prove que each zone outdoor air flow is right , or it is ok if the redbourn the total amount of outdoor air flow That Is entering in the room where the AHU is Placed ? Is this procedure right ?
PS.: Just to be clear, all the air of my zones are supplied by one AHU.
Thanks.
Dave Hubka
Practice Leader - SustainabilityEUA
LEEDuser Expert
534 thumbs up
February 16, 2016 - 12:09 pm
Hello Hugo, I do not entirely understand you question but will do my best to answer.
Project teams do not need to measure airflow at the zone level (e.g. airflow from supply diffusers serving the room) rather they need to measure the airflow at the system level (e.g. supply/return/outdoor air at the air handling unit).
I hope this helps.
Dave
Hugo Teixeira
Grupo OrionFebruary 16, 2016 - 1:34 pm
Precisely David. It is exactly what I was looking for .
Thanks very much .