Forum discussion

EBOM-2009 IEQp1:Minimum indoor air quality performance

Case 1 - Grouping the space types

Hi, we are working for the project with multiple tenants. we could not collect all the floors HVAC layouts. but we have the AHU details. we are grouping all the spaces as a office space. In calculation, we will enter only one office space for each AHU. Is it right way?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 12/16/2015 - 16:08

Entering only "office" into the calculator most likely won't be accepted by the LEED reviewer. When we do not have tenant build out plans we physically walk the space and measure potentially critical zones to enter into the 62MZ.

Mon, 02/15/2016 - 18:43

Hi David , I Understood your answer , but I would like to know if I must carry out the mesuruments for each zone in order to prove que each zone outdoor air flow is right , or it is ok if the redbourn the total amount of outdoor air flow That Is entering in the room where the AHU is Placed ? Is this procedure right ? PS.: Just to be clear, all the air of my zones are supplied by one AHU. Thanks.

Tue, 02/16/2016 - 17:09

Hello Hugo, I do not entirely understand you question but will do my best to answer. Project teams do not need to measure airflow at the zone level (e.g. airflow from supply diffusers serving the room) rather they need to measure the airflow at the system level (e.g. supply/return/outdoor air at the air handling unit). I hope this helps. Dave

Tue, 02/16/2016 - 18:34

Precisely David. It is exactly what I was looking for . Thanks very much .