NC-2009 SSc7.1:Heat island effect - nonroof

Carparking spaces located under ground level

We have 100% of carparking spaces located in 2 stories below ground level. All the roofs of the upper floor form the pedestrian hardscape for the plaza situated above. In addition the plaza is located 7 meters below ground level and it is an open space to sky. We would like to follow Option 2. Questions: 1) Can we consider the parking as underground parking spaces 2) Does the pedestrian hardscape have an SRI requirement? Thanks in advance for your help

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 05/06/2014 - 15:09

1) Yes, your parking will be considered 100% of spaces are underground. 2) The pedestrian hardscape should have an SRI of at least 29. If you have concrete you will meet this requirement as concrete is SRI 30.