Forum discussion

EBOM-v4 EQc2:Enhanced indoor air quality strategies

Carbon Dioxide Monitors

I currently have installed co2 sensors in densely occupied rooms located to the specifications mentioned in the OM LEED V4 Ref Guide. My query is how to calculate the ppm to which the sensors have to be set for each room installed

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 08/28/2017 - 22:07

Hi Sebastian, I don't have direct experience with this but the RG says "Determine CO2 concentration setpoint(s) using the methods in ASHRAE 62.1–2010, Appendix C. See ASHRAE 62.1–2010 User’s Manual, Appendix A, for calculations and examples." If you have an engineering consultant supporting you on IEQp1 I suggest working with them.