We are going through the third party reviewer portion of the credit and have one final hiccup. A garage type space is heated and conditioned with an energy recovery unit with gas heating. The baseline system is modeled with a constant volume rooftop unit with an ERV wheel, same as the proposed, but gas heating and DX cooling.

The reviewer is now stating that since the baseline system has cooling, then the proposed (built by now) building needs cooling. ASHRAE 90.1-1999 is the design guide line and section 11.4.3(d) was quoted as stating this is the design criteria. My version of ASHRAE 90.1-1999 states, "Minimum outdoor air ventilation rates shall be the same for both the budget building design and the proposed building. Heat recovery shall be modeled for the budget building design in accordance with 6.3.6.1."

My question is does any one agree with the reviewer regarding the cooling requirement? If the inspector is correct, where do I find this in ASHRAE 90.1 as I cannot find it? Are there different versions of ASHRAE 90.1-1999?