Hello,
Our project is an adaptive reuse on an urban site that was previously about 95% impervious. We are increasing the area of vegetated space (the old parking lot is being demolished), collecting rainwater from about 6700 SF of the roof area, and creating a rain garden out of a vegetated parking island that is about 1800 SF. We had already put together the stormwater volume reduction calculations using the NRCS method before the team decided to add the rain garden (we had previously been considering pervious pavement for a section of the front driveway), and now we are having trouble determining the proper way to quantify the runoff that will now be directed to the rain garden in the calculations. We plan to slope a section of the paving which surrounds the rain garden towards the rain garden, but how should this be quantified? Should the volume of water which will be draining to the rain garden be subtracted from the Runoff Volume Total in the design case (assuming that we have properly accounted for the rain garden being able to handle that 2-year 24-hour design storm volume based on the inches/hour infiltration rate for the soil), or should the CN value for that section of the paving be changed?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Michael DeVuono
Regional Stormwater LeaderArcadis North America
LEEDuser Expert
186 thumbs up
March 4, 2012 - 9:14 pm
You take a volume reduction based on the dead storage of the raingarden.
Christine Robbins-Elrod
Studio Director5G Studio Collaborative,llc.
19 thumbs up
March 27, 2012 - 6:57 pm
Hi Mike, thanks! So we would subtract the dead storage of the rain garden after the runoff volume subtotal has been calculated using a CN value of 98 for the hardscape and a lower CN value for the rain garden that is based on the infiltration rate of the soil? Have you previously used this strategy on a SSc6.1 submission?
Michael DeVuono
Regional Stormwater LeaderArcadis North America
LEEDuser Expert
186 thumbs up
March 29, 2012 - 9:51 pm
Hi Christine,
I have not personally submitted any credits, ever. I'm a CE, specializing in stormwater. Many of my projects have attained various LEED status, using my SWM calcs.
Use this equation to solve for the runoff that will drain to the raingarden:
Q={((P-.2S)^2)/((P-.2S)+S))}
P=2yr 24/hr depth (get it from NOAA's website)
S=(1000/CN)-10
Use a CN of 98 for impervious....61 for Lawn areas.
Then solve for the raingarden volume to make sure the 2-year storm fits:
Dead Storage = {(Bed Area ft^2)(h)}+{(Bed Area)(Dsoil)(0.17)}
h=height of the inlet grate in the RG (should be no more than 9"
Dsoil = depth of amended soil. Should be no deeper than 4'