FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

Building without HVAC Systems Designed

I got comments back on the energy model for a building that has no HVAC systems designed at the time of completion of the C&S. One comment was that the cooling energy savings seemed too high. The other was that the system airflow and fan power in the baseline seemed too high compared to the proposed. For both cases I let the equipment capacities, airflow and fan power calculate out instead of specifying identical values. Since the baseline has a worse envelope, the higher sensible load led to much higher capacity, airflow and fan power. This made sense to me because the worse envelope would demand the higher capacity system. However, the comments from LEED appear to be rejecting this approach and suggesting that I need to use identical values, but it’s not 100% clear to me that this is the case. The comments do allow for a narrative to justify the method/inputs. I am wondering if my approach is justifiable from LEED's perspective; or if it would be considered absolutely incorrect, in which case I would have to make the capacities, airflow and fan power identical for both cases. I would greatly appreciate any input you may have. Thanks,

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 10/07/2013 - 16:10

In general you should be able to get credit for a better envelope. Sounds like the reviewer is perhaps questioning the amount of savings relative to the envelope improvements. While the general approach sounds right perhaps there is something else going on. What percent savings are you showing for cooling and fans? If the envelope is the only savings perhaps you could make the two models the same and see what your savings look like then. Do they still make sense?

Mon, 10/07/2013 - 16:56

The cooling savings was 30%. Fans were 27%. The only other thing the reviewer caught is that I was using the wrong system type. I was using system #4 PSZ-HP, when it should have been #3 PSZ-AC. But regardless of the impact that might have, my question is really about what LEED views as the correct approach for this. Allowing the coils and fans to be auto-sized and therefore different for each case, or specify them and making them identical for each case? I know that table G3.1 in 90.1 states that when no system has been specified, the baseline and proposed systems shall be identical which obviously applies to the system type and efficiency, but it’s unclear if that applies to elements that are auto-sized in the calculation such as the coils and fans. Do you think my argument that the worse envelope demands the higher capacity equipment should at least justify this approach? Thanks,

Mon, 10/07/2013 - 17:07

They would be auto-sized in both cases. Identical systems do not imply identical capacities.

Mon, 10/07/2013 - 18:37

Thanks - very helpful!