Hello all,
Two little questions:
1) If I had automatic internal draps, would I be obliged to simulate them in the baseline/proposed building?
2) Is it possible to consider, as for the lighting system, an occupancy sensor for the fan coil system (for example reducing at 90% the maximum fan's electric energy consumption)?
Thank you in advance!
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
March 18, 2013 - 12:18 pm
Ciao Fabio,
1. Always model the proposed as designed. The baseline would be without shades. See Table G3.1.1-5 Proposed (d). You could likely get away without modeling them if you can make the case that your results are conservative without them, which seems likely to me.
2. Yes you can. Sounds like you will need to do it as an exceptional calculation. You will need to back up the claim of savings with a study or other documentation.
FABIO VIERO
Head of SustainabilityManens S.p.A.
18 thumbs up
March 18, 2013 - 12:52 pm
Hi Marcus,
Don't you think that if I turned off the fan coil I could lose the temperature control (not acceptable for Leed)?
Thank you very much!
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
March 18, 2013 - 1:00 pm
I would assume that when the space is unoccupied your system would revert to the unoccupied temperature setting and cycle back on if it reached the unoccupied minimum set point.
I suppose you could have temperature control issues depending on how you model it. If you are concerned about too many unmet load hours there is one way to find out . . .