In our hotel project, most rooms are non-smoking. Do they comply or do we have to test on all rooms even when they are designated as non smoking?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $15.95 »
Hannah Bronfman
Senior Associate99 thumbs up
February 17, 2014 - 1:36 pm
Hi Emmanuel
From my experience, you only have to test the rooms that are designated as smoking rooms. And in some instances sampling is permitted. For example, we had a ~100 room hotel where smoking was allowed in some rooms, and we were able to demonstrate compliance by testing 1 in 7 smoking rooms where the layout was identical (i.e. all queen suits).
Best,
Hannah