Goodmorning,
i haven't understood how to consider the performance of the baseline's chiller: is it enough to consider a costant COP/IPLV ( tab. 6.8.1) or do i need a performance curve?
Thank you.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5907 thumbs up
January 16, 2012 - 10:27 am
Hello Fabio,
I think it is enough.
90.1 requires that the software has the capability for the chiller to follow a performance curve, not that you need to enter one for the baseline. So you enter the COP/IPLV and the IPLV is the part-load efficiency based on the weighted average performance at various load capacities. Not certain without some more digging but I have assumed that the software creates a curve based on the COP and IPLV entered.
I'll check around and let you know if I am not accurate or someone else feel free to correct me.
FABIO VIERO
Head of SustainabilityManens S.p.A.
18 thumbs up
January 16, 2012 - 10:44 am
Hello Marcus,
thanks a lot for your answer.
Have a nice day.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5907 thumbs up
January 18, 2012 - 8:57 am
To be more accurate the software would typically use a default curve adjusted to the COP/IPLV.