FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

Baseline's chiller performance curve

Goodmorning, i haven't understood how to consider the performance of the baseline's chiller: is it enough to consider a costant COP/IPLV ( tab. 6.8.1) or do i need a performance curve? Thank you.

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 01/16/2012 - 15:27

Hello Fabio, I think it is enough. 90.1 requires that the software has the capability for the chiller to follow a performance curve, not that you need to enter one for the baseline. So you enter the COP/IPLV and the IPLV is the part-load efficiency based on the weighted average performance at various load capacities. Not certain without some more digging but I have assumed that the software creates a curve based on the COP and IPLV entered. I'll check around and let you know if I am not accurate or someone else feel free to correct me.

Mon, 01/16/2012 - 15:44

Hello Marcus, thanks a lot for your answer. Have a nice day.

Wed, 01/18/2012 - 13:57

To be more accurate the software would typically use a default curve adjusted to the COP/IPLV.