I would like to get some feedback on how you all are interpreting Exceptions (c) and (d) under 90.1-2007 G3.1.1 Baseline HVAC System Type and Description. I have heard and seen differing standpoints from within my office, reviewing other energy models through the commissioning process, and looking through the CIR database.
Exception (c) allows certain zones to be modeled as contant volume even though the primary baseline system type is VAV. These zones are "having special pressurizaiton relationships, cross-contamination requirements, or code-required minimum circulation rates." I see this exception as being intended for mainly hospital and laboratory spaces.
If I have a lab with fume hoods or other hazardous materials that require a negative pressure relationship to adjacent spaces (and also a minimum circulation rate), does this exception apply?
Or if a lab has no fume hoods and no hazardous materials, but the Authority Having Jurisdiction mandates a specific air-change requirement, does this exception apply?
For labs with no air-change requirement, then I can see sticking with the 0.4 cfm/SF minimum or minimum ventilation rate and maintaining the VAV system type.
I also previously posted the question on Exception (d) about how to treat laboratory spaces with a minimum of 5000 cfm of exhaust. How are you applying this exception? Are you assuming this is the sum of lab spaces or individual lab spaces?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5924 thumbs up
November 12, 2010 - 9:56 am
Yes it can apply to the situations you describe. These exceptions are optionally applied to individual projects.
Evelyn Dicks, EI, CxA
Mechanical EngineerMoses and Associates
83 thumbs up
November 12, 2010 - 10:35 am
Thanks Marcus, but what happens when both (c) and (d) apply?
I guess you can look at it that when you separate the Exception (c) spaces as single systems, the exhaust rate would usually be below 5000 cfm. But what if there is a large lab suite on a single system, with greater than 5000 cfm of exhaust and also requiring special pressurization relationships and minimum circulation rates, where both Exceptions (c) and (d) apply?
I have submitted an interpretation request into ASHRAE and will post the response.
Cory Duggin
Senior Energy WizardTLC Engineering Solutions
53 thumbs up
April 22, 2015 - 11:59 am
I have a similar situation. What was the response to the interpretation request? What should be done when both exception (c) and (d) apply?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5924 thumbs up
April 22, 2015 - 12:34 pm
I just noticed my advise above is not correct. The exceptions must be applied to projects, they are not optional.
If it is a lab space then apply d, if not apply c.