Hello,
I've a doubt regarding modeling a monozone baseline system (system 4).
Table G3.1.1B states that system 4 are constant volume. However, when I performe autosizing, some of the systems have cooling coils with a cooling capacity greater than 32kW. As per section 6.4.3.10, b), should I model these systems as VAV (variable flow or 2-speed)?
Thank you all for your time!
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5925 thumbs up
January 30, 2019 - 11:56 am
All of the baseline systems should be constant volume fans. Table G3.1 will tell you when the mandatory provisions apply to the baseline.