CS-v4 EAp2:Minimum energy performance

Baseline HVAC system type

I'm currently working in a project of shopping mall (common areas + tenant areas) pursuing LEED certification (Core&Shell). For simulation purposes, the type of HVAC system for the baseline building can be determined for one of the following (with different results): 1) considering the area of all building (tenants + common areas). Result: system type 8 for tenants and system 4 for common areas (differ by more than 31,2 W/m2 in peak loads); 2) considering the area of each tenant unit separately and the common areas: Result: 1 system per tenant (type 8 or 4, depending on the area) and 1 system for common areas (type 4). These different approaches can lead to very different results in the global performance. Note that each tenant will install its own HVAC equipment. Can you help me identifying the correct approach? Thanks in advance,

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 11/22/2016 - 17:27

Sounds like #1 to me. You apply Table G3.1.1A to the predominate conditioned space which sounds like the stores/tenant spaces. You then apply any exceptions according to G3.1.1. You can subtract the area of the common area from the total area and reenter Table G3.1.1A if that makes a difference.