Baseline HVAC System for Floors with Conditioned Spaces with no Ventilation

Hi!
According to Appendix G if the system selected if Systems 5-10, each floor will be modelled with separate HVAC system. What if the floor contains spaces that are conditioned yet no ventilation is provided? Will I model those spaces with a separate HVAC with no outdoor air supply or I'll just include it to the overall system of that floor not declaring any DesignSpecification:OutdoorAir objects to zones?

Climate Zone:1A

Modeling Software: EnergyPlus

 

Regards,

 Pan Pan

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 07/29/2019 - 14:39

Separate system 3 or 4 should be used when the occupancy, process load, or schedule are significantly different. Section G3.1.1 doesn't list a scenario where ventilation will exclusively determine the baseline system type.  As for how to model ventilation in the baseline, I've used judgement in the past. When it's not critical, I'd just model it to be a percentage of total supply CFM on the system level. If it is critical, I'll model it on the zone level (which is more work!). That way, your baseline will account for the entire OA CFM and floor system will auto-size. I suggest you start by setting the zone OA for those zones not receiving ventilation to zero, and auto-size the rest, and see how it goes. 