Forum discussion

NC-v4 EAp2:Minimum energy performance

Baseline for Botanical Garden Areas of a Building

How do we model the baseline systems for an indoor botanical garden? The botanical garden requires a lot of glazing, but more so the HVAC system is really a process load in my opinion because it has to maintain the atmosphere of the plant types. Would you still use an ASHRAE baseline system?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 11/01/2024 - 03:03

In my experience such exotic thing are considered baseline and system selection is based on good filing your case for GBCI.  Am I right that it's not a big part of the project - like some 1000 sqf max and or not more that 1 % of GFA?

Fri, 11/01/2024 - 12:43

The botanical is 50% of the building area with dedicated HVAC to maintain 3 different climates in 3 separated atriums, so it is a substantial part of the building load

Fri, 11/01/2024 - 13:45

I agree that this is a process load. So you model the baseline the same as the proposed. If you want to claim any savings you would need to follow the exceptional calcualtion method.